Abstract
. The paper contains analysis of power factor
correction circuits that is made in the context of elaboration of
uninterruptable power supply system. Various correctors have
been estimated analytically, by means of simulation and
experimentally. The most significant attention has been paid to
the efficiency of the analyzed converters and their compatibility
with modular approach to development of power converters.
Keywords: uninterruptible power supply systems, power
factor, circuit simulation
I. INTRODUCTION
The proposed uninterruptable power supply system (UPSS)
provides a stable electrical supply for its load not only from
the mains or traditional energy storage - battery, but also from
alternative/extra energy resources like solar panels, fuel cells
or diesel-generator. In case of higher power demand (that is
usually temporary) UPSS may supply the load also from a
supercapacitor.
In order to get the maximum power from diesel-generator it
is very important to load it with sinusoidal current with no
phase shift. The same can be applied to the mains – its current
must be sinusoidal and purely active. To resolve the problem
of non-sinusoidal current an active rectifier with power factor
correction (PFC) must be used. This paper contains the
analysis of efficiency of various PFC circuits.
There are several commonly used topologies of PFC
circuits. Although they are quite different they contain similar
blocks of the transistors and/or diodes connected in series.
This makes a modular approach described, for example, in [1]
possible. The described modules include transistors
(connected as a half-bridge), their transistor drivers, circuits
for voltage/current measurements and interface for control
equipment. The utilized system developed in Riga Technical
University is similar, but has some significant differences [2]:
- modules include 2 DC-link capacitors connected in series
(Fig. 1-a) that allow testing half-bridge PFC circuits with
DC-link voltage up to 800V; One of capacitors can be
shunted if not necessary in the particular configuration;
- they provide voltage measurements on both DC-link
capacitors, helping to avoid voltage unbalance;
- they have optical control interface, to maximize control
device safety and control signal noise immunity;
- they have liquid cooling system that allow to minimize
volume of primary heat sinks.
For the given research the modules have been reconfigured
so that (Fig. 1-b) the third voltage is measured between the
midpoint of capacitors and the input connector. Thus
measurement of the input voltage of PFC becomes possible.
a) generalized configuration of the module;
b) configuration of module for the power factor corrector;
Fig. 1. Power board of versatile modular converter.
The modules can be controlled from ezDSP kit (with TI’s
TMS320 DSP) or dSpace DS1103 debugging hardware or
from any other control equipment via the corresponding
adaptor. However, the microprocessor training kit available in
the lab (with MCU MSP430) that has been utilized for the
purpose of initial debugging is directly compatible with the
modules. The dSpace control solution is preferable because it
offers excellent compatibility with Matlab-Simulink models
that fasten the debugging process.
II.SIMULATION OF PFC CONVERTERS
The initial estimation of PFC converters was made by
means of the simulation in Matlab-Simulink. For the faster
transfer from a model to control solution the models have
topology of the power modules. For this reason the Matlab-
Simulink models consist of the same 3 subsystems: power
converter, measurement board and control system. Driver
board is omitted in the model because power switches in
Matlab-Simulink model can be driven directly by logical
elements.
V.CONCLUSIONS
Six topologies of active PFC converter have been shortly
described, simulated and tested experimentally.
Simulation shows that the bridgeless and half-bridge
topologies have slightly higher efficiency and are good as PFC
circuits that correspond to the initial analytical estimation.
Both circuits at high power ensure input current with cos(f)
near 1, THD near 3-5%. At low power this circuits ensure
input current with cos(f) in range of 0.95-0.99 and THD in
range of 20-40%.
The half-bridge and full-bridge topologies allow ensures not
only power factor correction but also consuming of reactive
power of both types (capacitive/inductive). This phenomenon
can be used to compensate the reactive power of other devices
connected to the same grid.
Experimental result shows also that bridgeless topologies
have very high common-mode noise and need to be improved.
The reason of increased common-mode noise has to be
identified and removed. Fixing of this problem may lead to
significant improvement of the results of the bridgeless
topologies of PFC.
Interleaved boost converter has a big potential of
improvement because of the compensation of the current
ripple in parallel boost branches as it has been shown through
simulation. This topology, however, requires some additional
experimental investigation.
Scientific Journal of Riga Technical University
Power and Electrical Engineering
2010
_________________________________________________________________________________________________________________________ Volume 27
132
The overall conclusion after the experiments gives the
preference to the boost bridge topology due to its simple
construction and control providing at the same time high
efficiency and a rather small THD. Implementation of the
other PFC rectifiers requires an advanced investigation of
these converters.