Power System Engineering
1370367403-PowerSystemEngineering.ppt (Size: 1.09 MB / Downloads: 28)
Syllabus
Unit 1 TL Parameters
Unit 2 Modeling and performance of TLs
Unit 3 Transmission systems
Unit 4 Insulators and Cables
Unit 5 Distribution system
Unit 6 substation practice
Unit 1 TL Parameters
Parameters of single and three phase transmission lines with single and double circuits:
Resistance, inductance and capacitance of solid, stranded and bundle conductors
Symmetrical and unsymmetrical spacing
Transposition
Application of self and mutual GMD
Skin and proximity effect
Inductive interference with neighboring circuits.
Typical configuration ,conductor types and electrical parameters of 400,220,110,66 and 33 kV lines
Load Dispatch Centre
Five Load dispatch centre
Eastern Region Load Despatch Centre, Kolkatta
North Eastern Region Load Despatch Centre, Shillong
Northern Region Load Despatch Centre, New Delhi
Southern Region Load Despatch Centre, Bangaluru
Western Region Load Despatch Centre, Mumbai
Power Demand
17th Electrical Power Survey of India, 2007[1,2]
– Power demand rise to peak value of 153 GW (1,52,746 MW) by 2011-12.
– India needs a generation capacity of at least 200 GW (2, 00,000 MW) to be installed by 2012 from the present level of 114 GW (1, 14,000 MW)
McKinsey & Company’s - “Powering India: The Road to 2017” [3, 4]
– India grows at an average rate of 8% for the next 10 years
– Power demand likely to soar from around 114 GW at present to 315 to 335 GW by 2017.
– Needs generation capacity of 415 to 440 GW
– 4 key factors behind the analysis are:[3, 4]
(i) Rise of industrial power demand,
(ii) Commercial demand rising at 14% over the next 10 years,
(iii) ‘Power for all by 2012’ and
(iv) the realization of demand suppressed due to load shedding
[b]Transmission line[/b]
World's Leading Power Transmission Utility - 79556 Ckt.Km line has increased from 3708 ckm in 1950 -132 Substations as on Sept 30,2010
Transmission lines at 800/765 kV, 400 kV, 220 kV & 132 kV EHVAC & +500 kV HVDC levels
About 51% of total power generated in the country is wheeled through this transmission network
TL Parameters
All transmission lines in power system exhibits electrical properties of R, L, C & g
L and C are due to effects of electro magnetic and electro static fields around the conductors
Shunt conductance accounts for leakage currents flowing across insulators and ionized path in the air. But leakage currents are negligible compared to the current flowing in the TL.
Effect of magnetic fields on TLs
If a conductor is carrying high alternating currents, the distribution of current is not evenly dispersed throughout the cross section of the conductor due to magnetic field effect. This effect is classified as skin and proximity effect.
Factors :
Nature of material,
Freq. of the system,
Diameter of wire,
Shape of wire
Skin Effect
If the conductor is composed of one or more concentric circular elements, then the centre portion of the conductor will be enveloped by a greater magnetic flux than those on the outside. Consequently the self induced back-emf will be greater towards the centre of the conductor, thus causing the current density to be less at the centre than the conductor surface. This extra concentration at the surface is known as skin effect, and results in an increase in the effective resistance/reactance of the conductor.
Skin effect is the tendency of an alternating electric current (AC) to distribute itself within a conductor so that the current density near the surface of the conductor is greater than that at its core.
Proximity Effect
The proximity effect also increases the effective resistance/reactance and is associated with the magnetic fields of two conductors which are close together. If each carries a current in the same direction, the halves of the conductors in close proximity are cut by more magnetic flux than the remote halves. Consequently the current distribution is not even throughout the cross-section, a greater proportion being carried by the remote halves. If the currents are in opposite directions, the halves in close proximity will carry the greater density of current.
Unit 2 Modeling and performance of TLs
Classification of lines:
Equivalent circuits for short, medium and long lines
Attenuation constants, phase constant, surge impedance
Transmission efficiency and voltage regulation
Real and reactive power flow in lines:
Power angle diagram
Surge impedance loading
loadability limits based on thermal loading, angle, voltage stability considerations
Shunt and series compensation
Ferranti effect and corona loss
Unit 3 Transmission systems
Mechanical design of transmission lines
Line sag,
string chart,
line support,
conductor material,
economic considerations of the transmission line
overhead line versus underground line.
Unit 4 Insulators and Cables
Insulators:
Types, Voltage distribution in insulator string and grading , improvement of string efficiency.
Cables:
Constructional features of HT & LT cables, dielectric stress and grading , Thermal characteristics
Unit 5 Distribution system
Different types of distributors – Selection of conductor sizes – radial and ring main systems – DC three wire systems – single fed and multi fed distribution systems ;
Unit 6 substation practice
Types of substations,- equipments in the substation - bus bar arrangements – substation protection against over voltages
References
Text books:
D.P.Kothari, I.J. Nagrath, Power System Engineering, Tata McGrawHill Publishing, 2nd edition, 2008.
V.K. Metha, Rohit Metha, Principles of Power system, S. Chand, 4th revised edition.
Syed A. Nasar, Electric Power Systems, Tata Mc Graw Hill Publishing.
References:William Stevenson, Elements of power system analysis”, Mc Graw Hill Company, 4th edition.I.J.Nagrath and D.Kothari,”modern power system analysis” Tata mc graw hill 2nd edition.C.L.wadhwa,’Electrical power system’, new age publications, 1998.Turan gonen, ’Electrical power distribution system engineering
www.pgcil.com
www.ntpc.org
www.cpri.org