SAFETY INSTRUCTIONS
Kiturami Manual.pdf (Size: 3.49 MB / Downloads: 35)
FOR YOUR SAFETY
Gasoline, as well as other flammable materials and liquids, and the vapors they produce are
extremely dangerous. Do not handle, use or store gasoline or other flammable or combustible
materials anywhere near or in the vicinity of a boiler or any other appliance.
WHAT TO DO IF YOU SMELL GAS
Do not try to light any appliance.
Do not touch any electrical switch; do not use any phone in your building.
Immediately call your gas supplier from a neighbor's phone. Follow the gas supplier's
instructions.
If you cannot reach your gas supplier, call the fire department.
SCALDS? FIRST AID
Remove clothes: Quickly remove
all wet clothing which can
contain the heat.
Immediately submerge the burnt
s area into cold water for 30
minutes to reduce the heat and
to prevent more serious burning.
Keep the injured person warm.
Call a medical service, describe the
situation and follow their advice.
LOCATION
Install in a separate boiler room if possible to prevent infiltration of flue gas into the living
space. This appliance is typically installed indoors to avoid freezing the boiler. If the boiler is
to be installed outdoors, provisions must be made to keep the appliance and its associated
piping from freezing.
HIGH ALTITUDE
The boiler is designed to operate to capacity in installations with 2000 feet off elevation or
less. As elevations higher than 2000 feet have less dense air, the unit is not capable of providing
its specified capacity. The affect of elevation will de-rate the input by approximately 3.5% per
1000 foot of elevation. At elevation greater than 2000 feet, the combustion of the boiler must
be checked with a calibrated combustion tester to ensure safe and reliable operation.
SAFETY INSTRUCTION
A periodic inspection done by qualified service personnel is recommended at least
once a year.
Perform routine inspections, maintenance or cleaning after closing the manual gas
shut-off valve, pulling out the power cord and cool down.
Inspect gas leaks frequently by using a soapy water solution at all connections and
fittings.