08-10-2012, 03:28 PM
Generator Voltage Regulation
ac volt generator.pdf (Size: 12.71 KB / Downloads: 457)
Functional Blocks
A typical analog voltage regulator is illustrated in the block diagram above and incorporates the following:
· A Sensing Circuit using a single- or three-phase, step-down potential (voltage) transformers and DC rectifier/
filter assembly supplies the Error Detector with a DC feedback voltage that is proportional to the AC output
of the generator.
· A zener diode is used to provide a constant DC Voltage Reference against which the feedback voltage is
compared. An external voltage adjustment potentiometer is also provided to permit fine voltage adjustments
to be made manually.
· The Error Detector circuit produces a DC output error voltage proportional to the difference between the
feedback and the reference (zener diode) voltage. The Stabilization Network also inputs the error detector
and is adjusted to match the response of the regulator to the inductive time constant of the generator to
provide quick, smooth response when generator load is increased or decreased.
· The Firing Circuit converts the DC error voltage to a phase-controlled pulse that provides firing for the SCR
Power Controller package.
· The SCR Power Controller provides a phase-controlled signal to the generator DC field which holds the
generator output voltage constant under varying load conditions. Depending on the type of generator excitation,
the DC field may be applied directly to the slip rings of a rotating DC field, to the stationary field of a
DC pilot exciter, or to the stationary field of a brushless excitation system. Both single-phase and three-phase
generators typically use a single-phase SCR rectifier assembly. Larger machines often use a pilot exciter, the
field of which is excited by the voltage regulator, so that the amount of current required from the regulator is
relatively small. Note: See the Electrician’s Notebook article “The Silicon Controlled Rectifier” for details on
a typical SCR phase-controlled system.
· Because solid-state generator controls require a voltage output from the generator before they can begin working,
a Build-Up Circuit is employed which bypasses the SCR’s until the generator output becomes sufficient
for the electronic control to take-over control of the system. In its simplest form, this build-up circuit may be
a relay or contactor, the coil of which is connected to the sensing circuit, with the contacts wired in parallel to
bypass the SCR’s until the generator output voltage rises to about 85% of normal. Residual magnetism in the
generator field provides sufficient magnetism for the initial generator build-up to occur. On systems where
sufficient residual magnetism is not retained.