Most building automation networks consist of a primary and secondary bus which connect high-level controllers (generally specialized for building automation, but may be generic programmable logic controllers) with lower-level controllers, input/output devices and a user interface (also known as a human interface device).
The primary and secondary bus can be BACnet, optical fiber, ethernet, ARCNET, RS-232, RS-485 or a wireless network.
Most controllers are proprietary. Each company has its own controllers for specific applications. Some are designed with limited controls: for example, a simple Packaged Roof Top Unit. Others are designed to be flexible. Most have proprietary software that will work with ASHRAE's open protocol BACnet or the open protocol LonTalk.
Some newer building automation and lighting control solutions use wireless mesh open standards (such as ZigBee). These systems can provide interoperability, allowing users to mix-and-match devices from different manufacturers, and to provide integration with other compatible building control systems.
Inputs and outputs are either analog or digital (some companies say binary).
Analog inputs are used to read a variable measurement. Examples are temperature, humidity and pressure sensor which could be thermistor, 4-20 mA, 0-10 volt or platinum resistance thermometer (resistance temperature detector), or wireless sensors.
A digital input indicates if a device is turned on or not. Some examples of a digital input would be a 24VDC/AC signal, an air flow switch, or a volta-free relay contact (Dry Contact).
Analog outputs control the speed or position of a device, such as a variable frequency drive, a I-P (current to pneumatics) transducer, or a valve or damper actuator. An example is a hot water valve opening up 25% to maintain a setpoint.
Digital outputs are used to open and close relays and switches. An example would be to turn on the parking lot lights when a photocell indicate it is dark outside.
[edit] Infrastructure
[edit] Controller
Controllers are essentially small, purpose-built computers with input and output capabilities. These controllers come in a range of sizes and capabilities to control devices commonly found in buildings, and to control sub-networks of controllers.
Inputs allow a controller to read temperatures, humidity, pressure, current flow, air flow, and other essential factors. The outputs allow the controller to send command and control signals to slave devices, and to other parts of the system. Inputs and outputs can be either digital or analog. Digital outputs are also sometimes called discrete depending on manufacturer.
Controllers used for building automation can be grouped in 3 categories. Programmable Logic Controllers (PLCs), System/Network controllers, and Terminal Unit controllers. However an additional device can also exist in order to integrate 3rd party systems (i.e. a stand-alone AC system) into a central Building automation system).
PLC's provide the most responsiveness and processing power, but at a unit cost typically 2 to 3 times that of a System/Network controller intended for BAS applications. Terminal Unit controllers are usually the least expensive and least powerful.
PLC's may be used to automate high-end applications such as clean rooms or hospitals where the cost of the controllers is less of a concern.
In office buildings, supermarkets, malls, and other common automated buildings the systems will use System/Network controllers rather than PLC's. Most System controllers provide general purpose feedback loops, as well as digital circuits, but lack the millisecond response time that PLC's provide.
System/Network controllers may be applied to control one or more mechanical systems such as an Air Handler Unit (AHU), boiler, chiller, etc., or they may supervise a sub-network of controllers. In the diagram above, System/Network controllers are often used in place of PLCs.
Terminal Unit controllers usually are suited for control of lighting and/or simpler devices such as a package rooftop unit, heat pump, VAV box, or fan coil, etc. The installer typically selects 1 of the available pre-programmed personalities best suited to the device to be controlled, and does not have to create new control logic.
Occupancy
Occupancy is one of 2 or more operating modes for a building automation system. Unoccupied, Morning Warmup, and Night-time Setback are other common modes.
Occupancy is usually based on time of day schedules. In Occupancy mode, the BAS aims to provides a comfortable climate and adequate lighting, often with zone-based control so that users on one side of a building have a different thermostat (or a different system, or sub system) than users on the opposite side.
A temperature sensor in the zone provides feedback to the controller, so it can deliver heating or cooling as needed.
If enabled, Morning Warmup (MWU) mode occurs prior to Occupancy. During Morning Warmup the BAS tries to bring the building to setpoint just in time for Occupancy. The BAS often factors in outdoor conditions and historical experience to optimize MWU. This is also referred to as Optimised Start.
An override is a manually-initiated command to the BAS. For example, many wall-mounted temperature sensors will have a push-button that forces the system into Occupancy mode for a set number of minutes. Where present, web interfaces allow users to remotely initiate an override on the BAS.
Some buildings rely on occupancy sensors to activate lighting and/or climate conditioning. Given the potential for long lead times before a space becomes sufficiently cool or warm, climate conditioning is not often initiated directly by an occupancy sensor.
Lighting
Lighting can be turned on, off, or dimmed with a building automation or lighting control system based on time of day, or on occupancy sensor, photosensors and timers.[1] One typical example is to turn the lights in a space on for a half hour since the last motion was sensed. A photocell placed outside a building can sense darkness, and the time of day, and modulate lights in outer offices and the parking lot.
Lighting is also a good candidate for Demand response, with many control systems providing the ability to dim (or turn off) lights to take advantage of DR incentives and savings.