18-04-2011, 04:25 PM
Loads on Tunnels.ppt (Size: 1.06 MB / Downloads: 506)
Loads on Tunnels
• The most important potential loads acting on underground structures are earth/rock pressures and water pressure.
• Live loads due to vehicle traffic on the surface can be safely neglected, unless the tunnel is a cut and cover type with a very small depth of overburden.
• It may be generally stated, that the dimensioning of tunnel sections must be effected either against the overburden weight (geostatic pressure) or against loosening pressure (i.e. the weight of the loosened zone, called also protective or Trompeter's zone).
Design approach should include these elements:
• Experience, incorporating features of empiricism based on an understanding of ground characteristics and on successful practices in familiar or similar ground.
• Reason, using analytical solutions, simple or more complex as the situation may demand, based on a comprehensive data on the ground conditions
• Observation of the behaviour of the tunnel during construction, developing into monitoring with systematic pre-designed modification of supports.
Types of rock pressure
• In nature, deep lying rocks, are affected by the weight of the overlying strata and by their own weight. These factors develop stresses in the rock mass. In general every stress produces a strain and displaces individual rock particles. But to be displaced, a rock particle needs to have space available for movement. While the rock is confined, thus preventing its motion, the stresses will be accumulated or stored in the rock and may reach very high values, far in excess of their yield point.
• As soon as a rock particle, acted upon by such a stored, residual or latent stress, is permitted to move, a displacement occurs which may take the form either of 'plastic flow' or 'rock bursts' (popping) depending upon the deformation characteristics of the rock-material.
• Whenever artificial cavities are excavated in rock the weight of the overlying rock layers will act as a uniformly distributed load on the deeper strata and consequently on the roof of the cavity.
• The resisting passive forces (shear strength) are scarcely mobilized prior to the excavation of the cavity, since the deformation of the loaded rock mass is largely prevented by the adjacent rocks. By excavating the cavity, opportunity is given for deformation towards its interior.
• In order to maintain the cavity the intrusion of the rock masses must be prevented by supporting structures.
• The load acting on the supports is referred to rock pressure. The determination of the magnitude or rock pressure is one of the most complex problems in engineering science.
• This complexity is due not only to the inherent difficulty of predicting the primary stress conditions prevailing in the interior of the non-uniform rock mass, but also to the fact that, in addition to the strength properties of the rock, the magnitude of secondary pressures developing after excavation around the cavity is governed by a variety of factors, such as the size of the cavity, the method of its excavation, rigidity of it support and the length of the period during which the cavity is left unsupported.
• Rock pressures depend not only on the quality of rock and on the magnitude of stresses and strains around the cavity, but also on the amount of time elapsing after the outbreak of the underground cavity.
• Within any particular rock the pressures to which it was exposed during its history are best indicated by the pattern of folds, joints and fissures, but it is difficult to determine how far these pressures are still latent.
• According to Terzaghi secondary rock pressure, should be understood as the weight of a rock mass of a certain height above the tunnel, which, when left unsupported would gradually drop out of the roof, and the only consequence of installing no support props would be that this rock mass would fall into the cavity. Successive displacements would result in the gradual development of an irregular natural arch above the cavity without necessarily involving the complete collapse of the tunnel itself.
• Earth pressure, on the other hand, would denote the pressure exerted by cohesionless, or plastic masses on the tunnel supports, without any pressure relief that would, in the absence of supports, sooner or later completely fill the cavity leading to its complete disappearance.
• In general, the magnitude of earth pressure is independent of the strength and installation time of the supporting structure and it is only its distribution that is affected by the deformation of the latter. The magnitude of rock pressures, on the other hand, is influenced decisively by the strength and time of installation of props.
• This is because the deformation following the excavation of the cavity in rock masses surrounding the tunnel is of a plastic nature and extends over a period of time. This period required for the final deformations and, thus for the pressures to develop, generally increases with the plasticity of the rock and with the depth and dimensions of its cross-section. The magnitude of deformations and consequently that of stresses can, therefore, be limited by sufficiently strong propping installed at the proper time.
• It should be remembered, however, that the intensity of plastic pressures shows a tendency to decrease with increasing deformations. Furthermore the loads are carried both by the tunnel lining and the surrounding rock and every attempt should be made to utilize this cooperation.
The reasons for the development of secondary rock pressures can be classified according to Rabcewicz in the following three main categories:
Loosening of the rock mass
• The weight of the overlying rock masses and tectonic forces
• Volume expansion of the rock mass, swelling due to physical or chemical action.
These reasons lead in general to the development of the following three types of rock pressure:
• Loosening pressure
• Genuine mountain pressure
Swelling pressure
The conditions under which rock pressures develop, the probability of their occurrence and their magnitude differ greatly from one another and require the adoption of different construction methods.
Rock pressure theories
There are various rock pressure theories; one group of rock pressure theories deal, essentially, with the determination of loosening pressure since the existence of any relationship between the overburden depth and mountain pressure is neglected. The group of theories that does not take the effect of depth into account are:
• Kommerell's theory
• Forchheimer's theory
• Ritter's theory
• Protodyakonov's theory
• Engesser's theory
• Szechy's theory
Another group of rock pressure theories takes into account the height of the overburden above the tunnel cavity. The group of theories that takes the effect of depth into account are:
• Bierbäumer's theory
• Maillart's theory
• Eszto's theory
• Terzaghi's theory
• Suquet's theory
• Balla's theory
• Jaky's Concept of theoretical slope
Vertical Loading -Bierbäumer's Theory
• Bierbäumer's theory was developed during the construction of the great Alpine tunnels. The theory states that a tunnel is acted upon by the load of a rock mass bounded by a parabola of height, h = aH.
Two methods, yielding almost identical results, were developed for the determination of the value of the reduction coefficient a.
One approach was to assume that upon excavation of the tunnel the rock material tends to slide down along rupture planes inclined at 45° + j/2
The weight of the sliding rock masses is counteracted by the friction force
S = 2fE = 2 tan F tan² (45° -F/2) •
developing along the vertical sliding planes and therefore a rock mass of height aH only, instead of H, must be taken into account during the calculations. Consequently, the pressure on width b + 2m tan (45° -F/2) at the crown will be:
p = a1H g
Taking into consideration the load diagram shown in Figure 3 the value of a1 is derived as follows:
Since
Thus
implying that geostatic pressure is diminished by the friction produced by the horizontal earth pressure of the wedges EC and DF acting on the vertical shear planes.
Values of the reduction coefficient for single and double-track tunnels, as well as for various angles of internal friction F and depths H are compiled in table 1.
The reduction coefficient a1 has two limit values, namely for very small overburden depths a = 1 and at several hundred metres depth, whenever H > 5B, the magnitude of a1 is no longer affected by depth and becomes
Terzaghi's vertical loading formula was based on a series of tests:
B, F, and g are the same as Bierbäumer.
K= 1 (based on his tests)
Determination of lateral pressures on tunnels
• The magnitude of lateral pressures has equal importance with the vertical or roof pressures for structural dimensioning of tunnel sections.
• The sidewalls of the cavity are often the first to fail owing to the less favourable structural conditions developing in the rock there. In some instances lateral pressure may play a more important role than the roof load.
• Also its theoretical estimation is more involved than that of the roof load, since its magnitude is even more affected by the extent of deformations of the section, so that its value depends increasingly on the strength of lateral support besides the properties of the rock and dimensions of the cavity.
• Lateral pressures are also much more affected by latent residual geological stresses introduced into the rock mass during its geological history which are released upon excavation and whose magnitude depends on the deformation suffered by, and the elasticity of the rock, but it is unpredictable. Genuine mountain pressure and swelling pressure that cannot be evaluated numerically may act in full on the sidewalls.
Approximate determination of lateral pressures:
• Lateral pressures in soils are determined approximately from earth pressure theory, as a product of geostatic pressure, or roof load and the earth pressure coefficient, respectively in terms of the lateral strain.
• Lateral pressures are (Stini) in contrast to roof loads, in a linear relationship with overburden depth. This has been confirmed also by recent model tests and in-situ stress measurements.
• At greater depths pressures on the springings are usually higher than on the roof, but at the same time frictional resistance is also higher.
Lateral pressures compiled according to practical experience are given in the table below:
• According to Terzaghi, a rough estimate of lateral pressure is given by the following formula:
• where hp is the height of the loosening core representing the roof load; in granular soils and rock debris, on the basis of Rankine's ratio
• and finally, in solid rocks, relying on Poisson’s ratio
• Lateral pressures should be assumed in a linear distribution and should be based on the vertical pressure estimated by one of the rock pressure theories instead of on geostatic pressure.
The parabolic distribution shown in below figure should be assumed for the vertical pressure having a peak ordinate corresponding to the estimated roof load.
If the pressure ordinate of the parabola an the vertical erected at the side of the cavity is , then the lateral pressure intensity at roof level will be
and at invert level
Owing to the favourable effect of lateral pressure on bending moments arising in the section, cohesion, which tends to reduce the magnitude of this pressure, must not be neglected in the interest of safety.
The lateral pressure coefficients involved in the above formulae are either
Bottom Pressures
• Bottom pressures should be essentially the counterparts of roof loads, i.e. reactions acting on the tunnel section from below if the tunnel section is a closed one having an invert arch.
• A certain part of this load is, however, carried by the surrounding rock masses, so that this situation does not occur even in the case of closed sections, and bottom pressures have usually been found to be smaller than roof loads.
• Terzaghi quoted empirical evidence indicating that bottom pressures are approximately one half and lateral thrusts one-third of the roof load intensity.
• In the case of sections open at the bottom, i.e. having no invert arch, pressures of different intensity develop under the side walls and under the unsupported bottom surface. The pressures arising under the solid side walls must be compared with the load-bearing capacity, or ultimate strength of the soil, but do not otherwise affect the design of the tunnel, The magnitude of rock pressure acting upward towards the interior of the open tunnel section is, however, unquestionably affected by these pressures .
• The development, distribution and magnitude of bottom pressures are greatly influenced by the method of construction adopted, i.e. by the sequence in which various structures and components of the tunnel are completed.
Bottom pressure according to Tsimbaryevitch
He assumed that a soil wedge is displaced towards the cavity under the action of active earth pressure originating from the vertical pressure on the lateral parts. This displacement is resisted by the passive earth pressure on the soil mass lying under the bottom of the cavity.
• The active earth-pressure diagram at the perpendicular of the corner point of the excavated cavity is a trapeze. The earth pressure at depth x will be
• At the same time the specific passive earth pressure at depth x is
• Depth x: where ea = ep can be computed by equating the above two expressions. The layers above this depth will be involved in bottom pressure:
The magnitude of the horizontal force acting towards the cavity above depth x is given as the difference between the areas of the diagrams for ea and ep. This force induces a set of sliding surfaces inclined at (45° - F/2) to develop in the soil mass under the cavity.
The force of magnitude E = Ea - Ep may be resolved into components T and S, parallel to the sliding surfaces and perpendicular to them, respectively:
T = E cos (45º - F/2)
S = E sin (45º - F/2)
Force T tends to displace the soil and is resisted by the frictional component of the normal force
T = S tan F
After trigonometric transformations and remembering that the soil is displaced by forces acting from both corners, the magnitude of forces acting on the bottom plane is obtained as:
The resultant To acts at the centre line and is vertical. This upward pressure can be counteracted either by loading the bottom with the counterweight of intensity qo, or by a suitably dimensioned invert arch.