11-11-2014, 10:57 AM
Abstracts: Energy is one of the major inputs for economic development of the industry. Energy sector assumes critical importance in a view of increasing energy need and requiring huge investment to meet them. Reduction in energy consumption helps industry to reduce its energy bill, improve system performance and enhance its competitive position. Energy consumption also has a significant impact on human environment, so it is require finding out ways of decreasing energy consumption. This report contains the Calculation of Thermal Design parameters of Evaporative condenser of refrigeration unit at Amul dairy, overview of refrigeration system arrangement at project site, industry problem, and Calculation of Thermal Design of Evaporative condenser. According to calculation, total condensing load is 1625.13 kw or 463TR. Tube outer diameter of condenser is selected from standard manufacturer’s catalog which is 26.67mm. Total heat transfer surface area in DE superheating section is 8.15m2 and in condensing area it is 330.28 m2. It is our belief that it will be helpful to industry.