THREE PHASE FAULT ANALYSIS WITH AUTO RESET FOR TEMPORARY FAULT AND TRIP FOR PERMANENT FAULT
1455782906-finalbasepaper.docx (Size: 464.95 KB / Downloads: 5)
Abstract
This paper to develop an automatic tripping mechanism for the three phase supply system. The project output resets automatically after a brief interruption in the event temporary fault while it remains in tripped condition in case of permanent fault. The electrical substation which supply the power to the consumers, have failures due to some faults which can be temporary or permanent. These faults lead to substantial damage to the power system equipment. In India it is common, The faults might be LG (Line to Ground), LL (Line to Line), 3L (Three lines) in the supply systems and these faults in three phase supply system can affect the power system. To overcome this problem a system is built, which can sense these faults and automatically disconnects the supply to avoid large scale damage to the control gears in the grid sub-stations. This system is built using three single phase transformers which are wired in star input and star output, and 3 transformers are connected in delta connections, having input 220 volt and output at 12 volt. This concept low voltage testing of fault conditions is followed as it is not advisable to create on mains line. 555 timers are used for handling short duration and long duration fault conditions. A set of switches are used to create the LL, LG and 3L fault in low voltage side, for activating the tripping mechanism. Short duration fault returns the supply to the load immediately called as temporary trip while long duration shall result in permanent trip. The concept in the future can be extended to developing a mechanism to send message to the authorities via SMS by interfacing a GSM modem.
I. Introduction
Various studies have shown that anywhere from 70%, to as high as 90%, of faults on most overhead lines are transient. A transient fault, such as an insulator flashover, is a fault which is cleared by the immediate tripping of one or more circuit breakers to isolate the fault, and which does not recur when the line is re-energized. Faults tend to be less transient (near the 80% range) at lower, distribution voltages and more transient (near the90% range) at higher, sub transmission and transmission voltages.
Lightning is the most common cause of transient faults, partially resulting from insulator flashover from the high transient voltages induced by the lightning. Other possible causes are swinging wires and temporary contact with foreign objects. Thus, transient faults can be cleared by momentarily de- energizing the line, in order to allow the fault to clear.Autoreclosing can then restore service to the line.
The remaining 10 - 30% of faults are semi- permanent or permanent in nature. A small branch falling onto the line can cause a semi-permanent fault. In this case, however, an immediate de-energizing of the line and subsequent auto reclosing does not clear the fault. Instead, a coordinated time-delayed trip would allow the branch to be burned away without damage to the system. Semi-permanent faults of this type are likely to be most prevalent in highly wooded areas and can be substantially controlled by aggressive line clearance programs.
Permanent faults are those that will not clear upon tripping and reclosing. An example of a permanent fault on an overhead line is a broken wire causing a phase to open, or a broken pole causing the phases to short together. Faults on underground cables should be considered permanent. Cable faults should be cleared without auto reclosing and the damaged cable repaired before service is restored. There may be exceptions to this, as in the case of circuits composed of both underground cables and overhead lines.
Although auto reclosing success rates vary from one company to another, it is clear that the majority of faults can be successfully cleared by the proper use of tripping and auto reclosing. This de- energizes the line long enough for the fault source to pass and the fault arc to de-energize, then automatically recloses the line to restore service. Thus, autoreclosing can significantly reduce the outage time due to faults and provide a higher level of service continuity to the customer. Furthermore, successful high-speed reclosing auto reclosing. on transmission circuits can be a major factor when attempting to maintain system stability. For those faults that are permanent, auto reclosing will reclose the circuit into a fault that has not been cleared, which may have adverse affects on system stability (particularly at transmission levels).
II. VOLTAGE REGULATOR
The LM78XX/LM78XXA series of three- terminal positive regulators are available in the TO- 220/D-PAK package and with several fixed output voltages, making them useful in a Wide range of applications. Each type employs internal current limiting, thermal shutdown and safe operating area protection, making it essentially indestructible. If adequate heat sinking is provided, they can deliver over 1A output Current. Although designed primarily as fixed voltage regulators, these devices can be used
IV. HARDWARE TESTING
1. Conductivity Test:
In electronics, a continuity test is the checking of an electric circuit to see if current flows (that it is in fact a complete circuit). A continuity test is performed by placing a small voltage (wired in series with an LED or noise-producing component such as a piezoelectric speaker) across the chosen path. If electron flow is inhibited by broken conductors, damaged components, or excessive resistance, the circuit is "open".
Devices that can be used to perform continuity tests include multi meters which measure current and specialized continuity testers which are cheaper, more basic devices, generally with a simple light bulb that lights up when current flows.
An important application is the continuity test of a bundle of wires so as to find the two ends belonging to a particular one of these wires; there will be a negligible resistance between the "right" ends, and only between the "right" ends.
This test is the performed just after the hardware soldering and configuration has been completed. This test aims at finding any electrical open paths in the circuit after the soldering. Many a times, the electrical continuity in the circuit is lost due to improper soldering, wrong and rough handling of the PCB, improper usage of the soldering iron, component failures and presence of bugs in the circuit diagram. We use a multi meter to perform this test. We keep the multi meter in buzzer mode and connect the ground terminal of the multi meter to the ground. We connect both the terminals across the path that needs to be checked. If there is continuation then you will hear the beep sound.
2. Power ON Test:
This test is performed to check whether the voltage at different terminals is according to the requirement or not. We take a multi meter and put it in voltage mode. Remember that this test is performed without ICs. Firstly, if we are using a transformer we check the output of the transformer; whether we get the required 12V AC voltage (depends on the transformer used in for the circuit). If we use a battery then we check if the battery is fully charged or not according to the specified voltage of the battery by using multimeter.
Then we apply this voltage to the power supply circuit. Note that we do this test without ICs because if there is any excessive voltage, this may lead to damaging the ICs. If a circuit consists of voltage regulator then we check for the input to the voltage regulator (like 7805, 7809, 7815, 7915 etc) i.e., are we getting an input of 12V and a required output depending on the regulator used in the circuit. EX: if we are using 7805 we get output of 5V and if using 7809 we get 9V at output pin and so on.
This output from the voltage regulator is given to the power supply pin of specific ICs. Hence we check for the voltage level at those pins whether we are getting required voltage. Similarly, we check for the other terminals for the required voltage. In this way we can assure that the voltage at all the terminals is as per the requirement.
VI. CONCLUSION
This project is designed in the form of Hardware for three single phase transformers 230v to 12V of output for to develop an automatic tripping mechanism for the three phase supply system while temporary fault and permanent fault occurs. Here we used 555 timer with relay for the fault is temporary or permanent.
Short duration fault returns the supply to the load immediately called as temporary trip while long duration shall result in permanent trip. The concept in the future can be extended to developing a mechanism to send message to the authorities via SMS by interfacing a GSM modem.