Implementation of Flux-Charge Control Model to Multifunctional Dynamic Voltage Restorer for Emergency Control in Distribution Systems
1Implementation of Flux-Charge.pdf (Size: 465.82 KB / Downloads: 33)
ABSTRACT:
The dynamic voltage restorer (DVR) is one of the modern devices used in distribution systems to protect consumers against sudden changes in voltage amplitude. In this paper, emergency control in distribution systems is discussed by using the proposed multifunctional DVR control strategy. Also, the multi loop controller using the Posicast and P+Resonant controllers is proposed in order to improve the transient response and eliminate the steady-state error in DVR response, respectively. The proposed algorithm is applied to some disturbances in load voltage caused by induction motors starting, and a three-phase short circuit fault. Also, the capability of the proposed DVR has been tested to limit the downstream fault current. The current limitation will restore the point of common coupling (PCC) (the bus to which all feeders under study are connected) voltage and protect the DVR itself.
INTRODUCTION
Voltage sag and voltage swell are two of the most important power-quality (PQ) problems that encompass almost 80% of the distribution system PQ problems. According to the IEEE 1959–1995 standard, voltage sag is the decrease of 0.1 to 0.9 p.u. in the rms voltage level at system frequency and with the duration of half a cycle to 1 min. Short circuits, starting large motors, sudden changes of load, and energization of transformers are the main causes of voltage sags [3]. According to the definition and nature of voltage sag, it can be found that this is a transient phenomenon whose causes are classified as low- or medium-frequency transient Events. In recent years, considering the use of sensitive devices in modern industries, different methods of compensation of voltage sags have been used. One of these methods is using the DVR to improve the PQ and compensate the load voltage.
DVR COMPONENTS AND ITS BASIC
OPERATIONAL PRINCIPLE A. DVR Components A typical DVR-connected distribution system is shown in Fig. 1, where the DVR consists of essentially a series-connected injection transformer, a voltage-source inverter, an inverter output filter, and an energy storage device that is connected to the dc link. Before injecting the inverter output to the system, it must be filtered so that harmonics due to switching function in the inverter are eliminated. It should be noted that when using the DVR in real situations, the injection transformer will be connected in parallel with a bypass switch (Fig. 1). When there is no disturbances in voltage, the injection transformer (hence, the DVR) will be short circuited by this switch to minimize losses and maximize cost effectiveness. Also, this switch can be in the form of two parallel thyristors, as they have high on and off speed. A financial assessment of voltage sag events and use of flexible ac transmission systems (FACTS) devices, such as DVR, to mitigate them is provided in. It is obvious that the flexibility of the DVR output depends on the switching accuracy of the pulse width modulation (PWM) scheme and the control method. The PWM generates sinusoidal signals by comparing a sinusoidal wave with a saw tooth wave and sending appropriate signals to the inverter switches.
PROPOSED MULTIFUNCTIONAL DVR
In addition to the aforementioned capabilities of DVR, it can be used in the medium-voltage level (as in Fig. 6) to protect a group of consumers when the cause of disturbance is in the downstream of the DVR’s feeder and the large fault current passes through the DVR itself. In this case, the equipment can limit the fault current and protect the loads in parallel feeders until the breaker works and disconnects the faulted feeder. The large fault current will cause the PCC voltage to drop and the loads on the other feeders connected to this bus will be affected. Furthermore, if not controlled properly, the DVR might also contribute to this PCC voltage sag in the process of compensating the missing voltage, hence further worsening the fault situation.
CONCLUSION
In this paper, for improving the transient response and
eliminating the steady-state error, the Posicast and
P+Resonant controllers are used. As the second function of
this DVR, using the flux-charge model, the equipment is
controlled so that it limits the downstream fault currents
and protects the PCC voltage during these faults by acting
as variable impedance.The simulation results verify the
effectiveness and capability of the proposed DVR in
compensating for the voltage sags caused by short circuits
and the large induction motor starting and limiting the
downstream fault currents and protecting the PCC voltage.