12-12-2012, 06:19 PM
OVERCURRENT and EARTH FAULT RELAYS
OVERCURRENT.pdf (Size: 17.05 KB / Downloads: 154)
Theory:
The function of a relay is to detect abnormal conditions in the system and to initiate
through appropriate circuit breakers the disconnection of faulty circuits so that
interference with the general supply is minimised. Relays are of many types. Some
depend on the operation of an armature by some form of electromagnet. A very
large number of relays operate on the induction principle. When a relay operates it
closes contacts in the trip circuit which is normally connected across 110 V D.C.
supply from a battery. The passage of current in the coil of the trip circuit actuates
the plunger, which causes operation of the circuit breaker, disconnecting the faulty
system.
In the laboratory, a 3-phase contactor simulates the operation of the circuit breaker.
The closure of the relay contacts short-circuits the 'no-volt ' coil of the contactor,
which, in turn, disconnects the faulty system.
The protective relaying which responds to a rise in current flowing through the
protected element over a pre-determined value is called 'overcurrent protection' and
the relays used for this purpose are known as overcurrent relays. Earth fault
protection can be provided with normal overcurrent relays, if the minimum earth
fault current is sufficient in magnitude. The design of a comprehensive protection
scheme in a power system requires the detailed study of time-current characteristics
of the various relays used in the scheme. Thus it is necessary to obtain the timecurrent
characteristics of these relays.
The overcurrent relay works on the induction principle. The moving system consists
of an aluminium disc fixed on a vertical shaft and rotating on two jewelled bearings
between the poles of an electromagnet and a damping magnet. The winding of the
electromagnet is provided with seven taps (generally0, which are brought on the
front panel, and the required tap is selected by a push-in -type plug. The pick-up
current setting can thus be varied by the use of such plug multiplier setting. The
pick-up current values of earth fault relays are normally quite low.
The operating time of all overcurrent relays tends to become asymptotic to a definite
minimum value with increase in the value of current. This is an inherent property of
he electromagnetic relays due to saturation of the magnetic circuit. By varying the
point of saturation, different characteristics can be obtained and these are
1. Definite time
2. Inverse Definite Minimum Time (IDMT)
3. Very Inverse
4. Extremely Inverse
The torque of these relays is proportional to f1f2 Sina, where f1 and f2 are the
two fluxes and a is the angle between them. Where both the fluxes are produced by
the same quantity (single quantity relays) as in the case of current or voltage
operated, the torque T is proportional to I2, or T = K I2, for coil current below
saturation. If the core is made to saturate at very early stages such that with increase
of I, K decreases so that the time of operation remains the same over the working
range. The time -current characteristic obtained is known as definite -time
characteristic.
If the core is made to saturate at a later stage, the characteristic obtained is known as
IDMT. The time-current characteristic is inverse over some range and then after
saturation assumes the definite time form. In order to ensure selectivity, it is
essential that the time of operation of the relays should be dependent on the severity
of the fault in such a way that more severe the fault, the less is the time to operate,
this being called the inverse-time characteristic. This will also ensure that a relay
shall not operate under normal overload conditions of short duration.
It is essential also that there shall be a definite minimum time of operation, which
can be adjusted to suit the requirements of the particular installation. At low values
of operating current the shape of the curve is determined by the effect of the
restraining force of the control spring, while at high values the effect of saturation
predominates. Different time settings can be obtained by moving a knurled
clamping screw along a calibrated scale graduated from 0.1 to 1.0 in steps of 0.05.
This arrangement is called Time Multiplier Setting and will vary the travel of the
disc required to close the contacts. This will shift the time-current characteristic of
the relay parallel to itself.
By delaying the saturation to a further point, the Very Inverse and Extremely Very
Inverse time current characteristics can be obtained.
Pre-experimental quiz
1. What do you understand by
· Primary relay
· Secondary relay
· Auxiliary relay?
2. What do you understand by
· Single quantity relay
· Double or multiple quantity relay?
3. What is the purpose of shaded pole structure?
4. Can both a.c and d.c actuate the overcurrent & earth fault relays?
5. What is meant by
· Pick-up current
· Drop-out current
· Dropout ratio?
6. In systems with low ground fault current is there a necessity to provide an earth
fault relay?
7. Where do you connect overcurrent & earth fault relays in a power system?
8. What do sensitivity & selectivity of a relay mean?
Material & equipment
Overcurrent relay, Earth fault relay, Current transformer, 3-phase contactor, 1-phase
load, Ammeter, Digital timer.