1. Scope
The work shall consist of furnishing and placing steel reinforcement for reinforced concrete or pneumatically applied mortar.
2. Material
Steel reinforcement shall conform to the requirements of Section 835, Steel Reinforcement, of the latest edition of the Alabama Department of Transportation Standard Specifications for Highway Construction. Before reinforcement is placed, the surface of the bars and fabric and any metal supports shall be cleaned to remove any loose, flaky rust, mill scale, oil, grease, or other undesirable coatings or foreign substances. Epoxy-coated steel reinforcement shall be free of surface damage. After placement, the reinforcement shall be maintained in a clean and serviceable condition until it is completely embedded within the concrete.
3. Bar schedule, lists and diagrams
Any supplemental bar schedules, bar lists or bar-bending diagrams required in section 10 of this specification to accomplish the fabrication and placement of steel reinforcement shall be provided by the contractor. Before reinforcement is placed, the contractor shall furnish four copies of any such lists or diagrams to the contracting officer for approval. Acceptance of the reinforcement is not based on approval of these lists or diagrams, but on inspection of the steel reinforcement after it has been placed, tied, and supported and is ready to receive concrete.
4. Bending
Reinforcement shall be cut and bent in compliance with the requirements of the American Concrete Institute Standard 315. Bars shall not be bent or straightened in a manner that will injure or weaken the material. Bars with kinks, cracks, or improper bends will be rejected.
5. Splicing bar reinforcement
Splices of reinforcement shall be made only at locations shown on the drawings and provided by the steel schedule. Placement of bars at the lap splice locations shown, when not in contact, shall not be farther apart than one-fifth the shown lap length and in any case no greater than 6 inches.
6. Splicing welded wire fabric
Unless otherwise specified, welded wire fabric shall be spliced in the following manner:
End-to-end—Adjacent sections shall be spliced end-to-end (longitudinal lap) by overlapping a minimum of one full mesh plus 2 inches plus the length of the two end overhangs. The splice length is measured from the end of the longitudinal wires in one piece of fabric to the end of the longitudinal wire in the lapped piece of fabric.
Side-to-side—Adjacent sections shall be spliced side to side (transverse lap) a minimum of one full mesh plus 2 inches. The splice length shall be measured from the centerline of the first longitudinal wire in one piece of fabric to the centerline of the first longitudinal wire in the lapped piece of fabric.
7. Placing
Reinforcement shall be accurately placed and secured in position to prevent its displacement during the placement of concrete. Tack welding of bars is not permitted. Metal chairs, metal hangers, metal spacers, and concrete chairs may be used to support the reinforcement. Metal hangers, spacers, and ties shall be placed in such a manner that they are not exposed in the finished concrete surface. The legs of metal chairs or side form spacers that may be exposed on any face of slabs, walls, beams, or other concrete surfaces shall have a protective coating or finish. The coating or finish can be hot dip galvanizing, epoxy coating, plastic coating, or stainless steel. Metal chairs and spacers not fully covered by a protective coating or finish shall have a minimum cover of 0.75 inch of concrete over the unprotected metal part. The exception is that those with plastic coatings may have a minimum cover of 0.5 inch of concrete over the unprotected metal part. Precast concrete chairs shall be manufactured of the same class of concrete as specified for the structure and shall have the tie wires securely anchored in the chair or a V-shaped groove at least 0.75 inch in depth molded into the upper surface to receive the steel bar at the point of support. Precast concrete chairs shall be clean and moist at the time concrete is placed.
High density or structural plastic rebar accessories designed to ensure maximum concrete bond may be substituted for metal or concrete accessories in spacer applications as approved by the contracting officer. Exposure of plastic rebar accessories at the finished concrete surface shall be kept to a minimum. Plastic rebar accessories, when used, shall be staggered along adjacent parallel bars and shall be placed at intervals no closer than 12 inches. Plastic rebar accessories shall not be used in concrete sections 6 inches or less in thickness.
Reinforcement shall not be placed until the prepared site has been inspected and approved. After placement of the reinforcement, concrete shall not be placed until the reinforcement has been inspected and approved by the contracting officer's technical representative (COTR).
8. Storage
Steel reinforcement stored at the work site shall be placed on platforms, skids, or other supports. This is done so that contact with the ground is avoided and the material is protected from mechanical damage and/or corrosion.
9. Measurement and payment
Method 1—For items of work for which specific unit prices are established in the contract, the weight of steel reinforcement placed in the concrete in accordance with the drawings is determined to the nearest pound by computation from the placing drawings. Measurement of hooks and bends is based on the requirements of ACI Standard 315. Computation of weights of reinforcement is based on the unit weights established in tables 34–1 and 34–2 of this specification. Computation of weights for welded wire fabric not shown in table 34–2 shall be based on ACI Standard 315. The area of welded wire fabric reinforcement placed in the concrete in accordance with the drawings is determined to the nearest square foot by computation from the placing drawings with no allowance for required laps. The weight of steel reinforcing in extra splices or extra-length splices approved for the convenience of the contractor or the weight of supports and ties is not included in the measurement for payment.
Payment for furnishing and placing reinforcing steel is made at the contract unit price. Such payment constitutes full compensation for all labor, material, equipment, and all other items necessary and incidental to the completion of the work including preparing and furnishing bar schedules, lists, or diagrams; furnishing and attaching ties and supports; and furnishing, transporting, storing, cutting, bending, cleaning, and securing all reinforcements.
Method 2—For items of work for which specific unit prices are established in the contract, the weight of bar reinforcement placed in the concrete in accordance with the drawings is determined to the nearest pound by computation from the placing drawings. Measurement of hooks and bends is based on the requirements of ACI Standard 315. Computation of weights of bar reinforcement is based on the unit weights established in table 34–1 of this specification. The weight of steel reinforcing in extra splices or extra length splices approved for the convenience of the contractor or the weight of supports and ties is not included in the measurement for payment.