24-12-2012, 06:10 PM
Limit State of Serviceability
![Adobe Acrobat PDF .pdf](https://seminarproject.net/images/attachtypes/pdf.gif)
Introduction
Structures designed by limit state of collapse are of comparatively smaller sections than those designed employing working stress method. They, therefore, must be checked for deflection and width of cracks. Excessive deflection of a structure or part thereof adversely affects the appearance and efficiency of the structure, finishes or partitions. Excessive cracking of concrete also seriously affects the appearance and durability of the structure. Accordingly, cl. 35.1.1 of IS 456 stipulates that the designer should consider all relevant limit states to ensure an adequate degree of safety and serviceability. Clause 35.3 of IS 456 refers to the limit state of serviceability comprising deflection in cl. 35.3.1 and cracking in cl. 35.3.2. Concrete is said to be durable when it performs satisfactorily in the working environment during its anticipated exposure conditions during service. Clause 8 of IS 456 refers to the durability aspects of concrete. Stability of the structure against overturning and sliding (cl. 20 of IS 456), and fire resistance (cl. 21 of IS 456) are some of the other importance issues to be kept in mind while designing reinforced concrete structures.
Control of Deflection
Clause 23.2 of IS 456 stipulates the limiting deflections under two heads as given below:
(a) The maximum final deflection should not normally exceed span/250 due to all loads including the effects of temperatures, creep and shrinkage and measured from the as-cast level of the supports of floors, roof and all other horizontal members.
(b) The maximum deflection should not normally exceed the lesser of span/350 or 20 mm including the effects of temperature, creep and shrinkage occurring after erection of partitions and the application of finishes.
It is essential that both the requirements are to be fulfilled for every structure.
For the deflection requirements
Different basic values of span to effective depth ratios for three different support conditions are prescribed for spans up to 10 m, which should be modified under any or all of the four different situations: (i) for spans above 10 m, (ii) depending on the amount and the stress of tension steel reinforcement, (iii) depending on the amount of compression reinforcement, and (iv) for flanged beams. These are furnished in Table 7.1.
For lateral stability
The lateral stability of beams depends upon the slenderness ratio and the support conditions. Accordingly cl. 23.3 of IS code stipulates the following:
(i) For simply supported and continuous beams, the clear distance between the lateral restraints shall not exceed the lesser of 60b or 250b2/d, where d is the effective depth and b is the breadth of the compression face midway between the lateral restraints.