Hot Weather Comparative Heat Balances in Pervious Concrete and Impervious Concrete Pavement Systems
1467505104-211340haselbachdoc.pdf (Size: 427.21 KB / Downloads: 17)
ABSTRACT
Many pavements contribute to the urban heat island (UHI) effect due to their bulk mass
and heat absorption capacities. Granular ground surfaces composed of soils or sands do not
contribute to the UHI effect in a similar manner. Their porous nature may lessen the effect both
with an increased insulating capacity and with an enhanced mechanism for evaporative cooling
from absorbed water.
Pervious concrete is a novel pavement which is being developed to aid in preventing
stormwater related environmental problems. Pervious concrete has a network of interconnected
voids which allow water exfiltration to the subbase below. Limited studies on pervious concrete
indicate that the pervious concrete surface can have elevated temperatures as compared to similar
traditional impervious pavements, but that temperatures are lower under the pavements.
This study focuses on a site in Iowa where both a pervious concrete and a traditional
concrete paving system have been installed and temperatures recorded within the systems for
extended time periods. The analyses cover days with negligible antecedent precipitation and high
air temperatures, extreme conditions for UHI impacts. This paper compares the increase in
overall heat stored during several diurnal heating cycles in both of these systems. These analyses
include not only the temperatures at various depths, but also the heat stored based on the bulk
mass of the various layers in each system and below grade. Results suggest that pervious
concrete pavement systems store less energy than traditional systems and can help mitigate the
urban heat island. (246 words)
Introduction
The urban heat island (UHI) effect has been studied in many cities and the contribution
from daytime heating is well established (Eliasson 1996, Asaeda et al. 1996, Pomerantz 2000).
Many traditional pavement types are known to be contributors to the urban heat island effect due
to their bulk mass and heat absorption capacities. Previous research has shown higher albedo
surfaces and shading can offset some of the impacts by reducing the solar energy absorbed in the
pavements (Akbari 2001). Lighter colors and higher albedos tend to aid in the mitigation of the
urban heat island by limiting solar energy absorbed into the system. The solar reflectance index
(SRI) is being used as a variable to compare the ‘coolness’ of various traditional pavements and
has been accepted by the US Green Building Council (USGBC) in its Leadership in Energy and
Environmental Design (LEED™) Green Building rating system as a methodology for
determining if a pavement design aids in mitigating the UHI effect (Haselbach 2008, Marceau
and Van Geem 2007). This variable is used independently of any other pavement parameter with
the assumption that the pavements compared have similar heat absorption and transfer
characteristics below the surface, although some studies acknowledge that subsurface
characteristics may be important (Gui et al. 2007).
Natural and manmade granular ground surfaces composed of soils or sands are not
considered to be contributors to the urban heat island effect due to their porous nature. Of
interest herein is the impact of the porosity of a pavement system on its capacity to absorb and
store energy. It has been suggested that the voids within highly pervious pavements may insulate
the ground, mitigating urban heat island impacts (Haselbach and Gaither 2008). Permeable
surfaces may also allow for evaporation of water that infiltrates into the media, also aiding in
cooling by evaporation.
There is a group of novel pavements referred to as permeable pavements which are being
developed to aid in preventing stormwater related environmental problems. Permeable
pavements allow stormwater to infiltrate into the ground, reducing runoff and avoiding costly
additional stormwater control devices to manage flooding and pollution dissemination
downstream. One such pavement is Portland Cement Pervious Concrete (PCPC), which provides
a hardscape similar to traditional impermeable concrete or asphalt pavements, but also consists
of a network of interconnected macro-pores which readily allow water exfiltration to the subbase
below and provide some water storage for further evaporation or infiltration. A question of
interest is how pervious concrete might perform due to its unique pore structure as compared to
traditional concrete under very hot conditions typical for the urban heat island.
Asaeda and Ca studied several surface media during two days of extreme heat in 1994.
Their results indicated that certain types of permeable pavements, particularly blocks, did not
necessarily aid in abetting the urban heat island effect. Detailed information was not given for all
the media used and therefore there was not a clear picture of how many of the porous pavements
might react (Asaeda and Ca 2000). There are only a few published studies on the temperature
impacts of using PCPC instead of other impervious pavement surfaces. From these it has been
shown that the PCPC surface can have elevated temperatures as compared with traditional
impervious pavements, but that temperatures decrease rapidly under the pavement (Haselbach
and Gaither 2008, Kevern et al. 2009a). None of the published studies have provided overall
energy balances for periods of extreme heat as compared to traditional pavements.
This study focuses on a site located at Iowa State University (ISU) where both a pervious
concrete and a traditional Portland Cement Concrete (PCC) paving system were installed and
temperature readings taken within the systems for extended time periods. The site was
constructed as part of the Iowa Pervious Concrete Stormwater project and also contained
monitors and collectors to quantify stormwater improvements observed from the pervious
concrete. The analysis covers days with typical high air temperatures greater than 32°C (90°F)
with negligible antecedent precipitation (no rain events in the previous 7-days), extreme
conditions for urban heat island impacts.
The pervious concrete, as compared to traditional concrete, is seen to have higher midpavement
temperatures at midday, but similar temperatures at these locations during the
night/early morning. However, in order to study urban heat island effects, the fluctuations in heat
storage over both of the complete systems should be evaluated to steady background soil
temperatures below the pavement systems. The analysis in this paper compares the overall heat
stored during several diurnal cycles in the summer throughout both of these systems. These
analyses include not only the temperatures at various depths, but also the heat stored based on
the bulk mass of the various layers in each system.
Although there are higher temperature readings near the surface in many of the pervious
concrete systems studied, these systems appear to have significantly higher below-grade
insulating capabilities than other traditional concrete systems. This may make it possible to
design pervious concrete systems to mediate or reverse additional urban heat island impacts
more effectively than traditional pavement surfaces.
Site Description
ISU parking lot 122 was constructed as the Department of Natural Resources Iowa
Pervious Concrete Water Quality Project, with the objective to quantify the environmental
impacts of pervious concrete parking areas. The site was designed to monitor both the quantity
and quality of stormwater effluent from equally-sized traditional and pervious concrete parking
areas. Temperature and soil moisture sensor arrays were installed in both of the pavement
profiles to monitor frost line penetration and infiltration characteristics. Water level sensors in
the pervious concrete aggregate bases coupled with monitoring wells allow estimation of
infiltration rates and the impact on local groundwater conditions. The site was constructed during
the summer and fall of 2006 and opened to traffic on December 4th, 2006. Sensors were installed
to compare the stormwater characteristics and thermal behavior of the two areas. Flow meters
and automated samplers were installed to measure and collect stormwater from the PCC surface
and from the PCPC base. Water level sensors in the aggregate bases and monitoring wells were
installed to determine actual infiltration and compare to theoretical values. Volumetric soil
moisture arrays were also installed under each pavement to determine infiltration characteristics.
Temperature sensor arrays (Campbell Scientific T107L) were installed into and underneath both
pavements to monitor thermal behavior. Surface sensors were omitted due to concerns with
winter plowing operations. The location and assigned names of the temperature sensor profiles
are shown in Figure 1 for both the PCPC and PCC pavements. Table 1 provides a description of
the sensors along with the depth below the pavement surface.
Methodology
As the sun’s energy is absorbed by the pavement, it warms. Later, the cooling cycle
begins and the pavement radiates heat when the temperature of the pavement surface becomes
greater than the temperature of the atmosphere above (e.g. the sun sets). The increased energy
required for air conditioning caused by the urban heat island effect is directly related to the
amount of energy absorbed and then released by the pavement system. A reduction in the total
energy stored in a pavement system will help mitigate this effect. To accurately compare the
energy stored in two systems, all energy storage calculations must be performed to a depth where
the temperatures are equal. For the two pavements discussed herein, at a depth of 60 cm below
the pavement surfaces the temperature difference was less than 1°C and assumed equal.
Equation 1 is used to calculate the amount of energy stored during the heating cycle of
the PCC system. The specific equations include the amount of heat stored in the pavement and
segregated soil layers corresponding to the temperature sensors. The first term represents the
energy stored in the traditional concrete. The average temperature of the PCC was taken as the
temperature recorded at mid-height in the pavement. The second term represents the energy
stored in the first 15cm of soil beneath the PCC pavement. The temperature in the first 15 cm
was taken as an average of the sensor located directly under the pavement and the sensor located
15 cm in the soil. The third term represents the energy stored in the soil between 15 cm and 45
cm beneath the PCC pavement. The temperature in this deeper layer was taken as the average
between the temperature recorded at 15cm beneath the pavement and the sensor located at 45 cm beneath the pavement.
Pervious Concrete System
The pervious concrete system consisted of 15 cm of pervious concrete over a 45 cm
compacted limestone aggregate base storage layer. The porosity of the pervious concrete was
measured as 31% (Kevern et al. 2009b). The traditional concrete was air entrained and porosity
was assumed at 5%. Therefore, the volumetric heat capacity of the pervious concrete was taken
as a proportion of solids versus the traditional concrete as in Equation 3.
CvPCPC = CvPCC (100-n)/100 (3)
Where:
CvPCPC is the adjusted volumetric heat capacity of the pervious concrete
CvPCC is the selected volumetric heat capacity of the concrete (2.1 J/cm3
°C)
n is the difference in porosity between the PCC and PCPC (31%-5% = 26%)
The dry density of the limestone base was measured as 1.44 g/cm3
. The specific heat
storage capacity of limestone was taken as 0.84 J/g°C, yielding a volumetric heat capacity of 1.2
J/cm3
°C (engineeringtoolbox 2009). A summary of the material property values used are shown
in Table 2.
Results
The typical daily temperatures at the mid-heights of both pavements and the air are
shown in Figure 2. During the day the temperature at mid-level in both pavements was always
warmer than the air temperature, with the PCPC approximately 5°C (9°F) warmer than the PCC
pavement right after the hottest period of the day. Although the PCPC was warmer during the
day, both pavements cooled to similar temperatures during the night.
The temperature behavior of the PCPC system with depth is shown in Figure 3 for the
same time period shown in Figure 2. The changes in the PCPC temperature followed closely
behind the air temperature variations, and temperatures fluctuated less with depth. The 60 cm
depth fluctuated less than 1°C over the analyzed time period.
The temperature behavior of the impervious PCC system with depth is shown in Figure 4
for the same time period as Figure 2 and Figure 3. The change in PCC temperature and the upper
layer of soil (15 cm below grade) are warmer than the air temperature, but follow a similar
heating trend. At 30 cm below grade the temperature response is buffered with only a slight daily
variation, with a significant phase lag as compared to the air temperature heating cycle.
Temperature at 60 cm below grade for both pavement types remained similar and constant.
The energy storage results for the selected days are shown in Table 3. Four of the days
had a heating cycle of 9 hours, while one had a heating cycle of 10 hours. For the five days
analyzed, the energy stored in the PCC system was greater than the energy stored in the PCPC
system, even though the PCPC pavement was warmer than the PCC pavement. This difference in
heat stored is a function of the higher porosity in both the PCPC and the aggregate base as
compared to the PCC and underlying soil respectively which lowered the PCPC system heat
capacity for similar volumes of the systems. On average the pervious concrete system stored
12% less energy than the traditional concrete from the surface to a background temperature
Conclusions
Temperature sensors were installed at various depths in adjacent pervious concrete and
traditional concrete systems. Temperature data for both systems were analyzed for five days
where the maximum temperature was greater than 32°C (90°F). All the analyses were conducted
for days with negligible antecedent precipitation. Bulk heat storage was calculated for the daily
heating phase using known values and values common in the literature for dry conditions of the
various layers in the pavement systems to a depth of a nearly constant background soil
temperature. Results show that less energy was stored during heating in the pervious concrete
system than the traditional concrete system. This was using similar cementitious mixtures for
both pavements (similar cement colors) and where, based on previous research, the pervious
concrete surface would have a lower solar reflectance and hence a higher surface temperature
under similar solar radiation conditions.
A strategy for mitigating the urban heat island effect may be to employ lower energy
storage pavement systems. Using pervious concrete systems with their layers of materials with
higher porosity than traditional pavement systems may be an effective tool in reducing the urban
heat island effect. Considerations of material characteristics below grade such as porosity are
important in determining a permeable pavement’s capacity for heat island mitigation. Solar
reflectance should not be used independent of these other variables.